I've been working my way through the Understanding The NEC vol. 1. I'm having a hard time understanding when and what C° column to use. I have copied and pasted the practice questions below. I've read through 110.14 and am still just not grasping it. I'd really appreciate some feed back. Thanks!!
Question #1: What size conductors rated 90°C are required between terminals rated 90°C for a circuit supplying a 44A continuous. load?
(a) 10 AWG
(b) 8 AWG
(c) 6 AWG
(d) 4 AWG
Question #2:
Question: What size XHHW-2 copper conductor can be used to interconnect 90°C rated power distribution blocks protected by a 400A overcurrent protective device serving a 320A continuous load?
(a) 250 kcmil (b) 300 kcmil (c) 350 kcmil (d) 400 kcmil
Side note: in case anyone has the Mike Holt understanding national electrical code volume one based on the 2020 NEC, and wants to physically see the questio, these questions are on page 77 and page 127.