Derating - NEC/NYC
TG3
New User
NYC
I see a lot of installations like such - 12-#10 Copper THHN CCC in 1” Conduit for 120V 20A Branch Circuits. For this purpose let’s say the loads on these 120V circuits are for general purpose receptacles and FCUs with a 20A max nameplate OCPD rating and a RLA of 10A lets say )
From what I gather, a lot of guys derate the #10 THHN from the 90Degree column @ 50% for the 10-20CCC and that equates to a final ampacity rating of 20A - and that math works at that point.
However, and please correct me if my understanding is wrong. But you must derate @ the weakest link amongst the circuit - which comes to be the termination points. Most terminals on 20A Breaker, 20A receptacle, the terminals inside the 20A FCU are rated at 75degrees. Those 12-#10 THHN derated @ 50% in the 75degree column is roughly 17.5A now.
I may be wrong but I think - going back to those specific loads I stated above - because the FCU is a fixed-load, the above installation would be NEC/NYC compliant. But the general purpose receptacle circuits would not be. The general purpose circuits/conductors feeding that circuit, must be able to handle the full 20A load. Therefore whichever of those 12-CCC are feeding the general purpose receptacles must be placed on a 15A breaker to become compliant.
The terminal doesnt get a 50% hit because there is no bundling at the terminal. So yes you use the weakest link, but derating from bundling is separate from termination limits.
you are derating the conductor, which is 90°C rated. that brings it down to 20a. the 75°C terminations determine that the circuit ampactiy will not end above the 75°C rating. which is 35a. so, realizing that the CONDUCTOR was derated to 20a. the terminations have a limit of 35a. your circuit ampacity is the least of the two. 20a.
The 90° C, #10 conductor after derating is a 20 amp conductor. The terminal value doesn't change that.
An electrical contractor got mad when I asked him if they make 120 volt bolt on circuit beakers in 5 or 7 amps because he used several existing 2" conduits from panels to a 12 by 12" 10' long existing ceiling trough after he pulled over 50 #10 THHW/THWN wires. Conduit was 12' long. It was for patient rooms in a large hospital and each room usually went overboard with 5 20 amp normal power receptacle circuits and at least three emergency npower 20 amp circuits. Months later I used my FLIR camera to check temperature of conduits. Was always within one degree of climate controlled electrical room.
I once did a grow house and had 3/4 emts with 9 #12 CCC running at 16 amps. The conduits were almost too hot to touch, but whatever the temp was was probably well below 194 degrees Fahrenheit.