Dale001289
Senior Member
- Location
- Georgia
We have a large bare copper EGC (500kCMIL) routed in a power cable tray for paralleled 350kCMIL feeders. There are three small dry type transformers (9-25kVA) solidly grounded installed along the same path as the cable tray.
The contractor wants to tie the transformer GECs to this EGC for sake of convenience rather than route the GECs directly to the grounding electrode system, (ground rods). Is this permissible?
The contractor wants to tie the transformer GECs to this EGC for sake of convenience rather than route the GECs directly to the grounding electrode system, (ground rods). Is this permissible?