As the code guy around here, I've been asked if it is compliant to install some 12 AWG supply-side taps, that is ahead of the service disconnect, for energy management meters. Let's say it's a 2000A switchboard. Is this complaint with the NEC?
The way I'm thinking about it is that if I we could tap the line side of the bus without voiding the listing, we could install another separate service disconnect just for the meters.Also of note: the only thing that references service taps is Article 230.46 (2023 Edition)
230.46 Spliced and Tapped Conductors.
Service-entrance conductors shall be permitted to be spliced or tapped in accordance with 110.14, 300.5(E), 300.13, and 300.15. Power distribution blocks, pressure connectors, and devices for splices and taps shall be listed. Power distribution blocks installed on service conductors shall be marked “suitable for use on the line side of the service equipment” or equivalent.
Pressure connectors and devices for splices and taps installed on service conductors shall be marked “suitable for use on the line side of the service equipment” or equivalent.
So other than making sure the devices used to make the tap are listed for use on service conductors, there really isn't much else in the way of code about service taps.
Yah, that'd work. Would be best to do the tap in a separate enclosure upstream of the switchgear probably (but in the same space). Something like this drawing perhaps? Just have to make sure to use devices that are rated for service use.The way I'm thinking about it is that if I we could tap the line side of the bus without voiding the listing, we could install another separate service disconnect just for the meters.
Love it. I think this would be the only way to make it complaint. Except that the 2000 in the switchboard would be the service disconnect. No service disconnect outside. The way it's drawn would be a grouping of service disconnect issue I believe.Yah, that'd work. Would be best to do the tap in a separate enclosure upstream of the switchgear probably (but in the same space). Something like this drawing perhaps? Just have to make sure to use devices that are rated for service use.