It is a rating for a 240V 2 wire source in addition to the normal rating for 120/240V 3 wire source.I think the phrase "additional rating" is the key to
I agree but I'm trying to think of a scenario where you would actually use that type of system to supply a panel. Two ungrounded legs of a corner grounded Delta?It says for a 2wire supply, 240V to ground, you cannot use slash rated breakers.
These types of manufacturer instructions were ignored for decades, until equivalent language was added to the NEC.
Yes. Or a single phase from a 2 phase system.Two ungrounded legs of a corner grounded Delta?