Rbarkema1
New User
- Location
- Des Moines Iowa
- Occupation
- Electrician
One of my coworkers asked me a question about junction box sizing for angle pull he said if I have 2 - 4inch EMT and 2 - 3inch EMT and those contain larger than 4awg conductors so they would certainly count for the box size calculation but if add 2 - 1inch EMT to the box that will not contain 4awg or larger conductors would I need to count them in my calculation. The 2026 code reads this distance shall be increased for additional entries by the amount of the sum of the diameters of all other raceway entries in the same row on the same wall of the box. looks like it says all other to me so I would count them I would like to hear your interpretation of this code article.