Forensic Analysis – Failed Transformer

GoldenstateEE

Member
Location
California
Occupation
Engineer
Hi all,
We recently had a failure of a dry-type indoor transformer and are exploring options for forensic analysis to better understand the failure mechanism.
Looking for recommendations on firms or labs that can support this type of work (teardown, material/microscopic analysis, failure determination, etc.).
Any suggestions or past experience would be appreciated. Thank you in advance.
 
Thats easy...
So what ocd tripped? Primary or secondary? Or did the whole neighborhood lose power?
What is primary/secondary voltage?
And who was the last idiot who fired it up?
Clearly human caused.
Looks like medium volt from here..
 
Jim, I have worked with you at Eaton. You worked at Eaton or Schneider? Frank Waterer used to perform these kind of analysis there.
I was at Schneider.

What does the center coil look like? I can't see much more than the fire damage.
What type of protective relay, does it save history?

Did you have critters nesting in there? What does the bottom of the enclosure look like.
 
I'm betting on failed insulation causing a shorted coil, drawing excessive current in that area, producing heat beyond the insulation rating, causing more shorted coils and so on. This can be caught with a differential relay and is regularly used on large oil filled transformers, but not on dry type.
 
This can be caught with a differential relay and is regularly used on large oil filled transformers, but not on dry type.
The keyword here is "large". Dry type transformers are not usually rated in MVA.

Evidently there was a protective relay, but it didn't operate before the fuses.
 