We are having a problem at one of our sites that has left a lot of our engineers, electricians, and others I've talked to about this scratching their heads. Want to run put it out there to see if anyone here has any thoughts.
Here is our setup: We installed a 600A 208V panelboard "PNLBD-1" in a parking lot. It is fed from the building service entrance by parallel runs of 500KCMIL phase conductors and #3/0 AWG GND. The PNLBD-1 feeds two vendor specific 400A 208V EV panelboards "EVPNL-1" and "EVPNL-2" that have branch circuits out to EV chargers. The run between PNLBD-1 and EVPNL-1 is parallel runs each with #4/0 AWG phase conductors and #3 AWG GND (we were limited by lug size the vendor provided us on the EVPNL so had to run parallel sets...) and the same for EVPNL-2. The run to EVPNL-1 is <10ft above grade in a trough since they're located right next to each other. The run to EVPNL-2 is ~100ft underground. The EVPNLs have power conductors and a low voltage signal wires that run from each EVPNL out to the EV chargers.
Here is our problem: The low voltage signal wire is seeing noise on the signal that is causing issues with the EV chargers. We have traced it down to an issue with the ground in EVPNLs. After some investigations and lots of measurement with a multimeter focusing mostly on EVPNL-2, we have found a very odd problem - when we disconnect the #3 AWG ground wires (in the parallel run between PNLBD-1 and EVPNL-2) on both ends so that it is hanging free at both panels but still run in the conduit, we are measuring voltage (~9V) on it with reference to the ground bus/enclosure/AG conduit/etc in PNLBD-1 (one lead on the ground wire and one on the other objects). When we measure the voltage between both ground wires still hanging free on both ends and each in their individual run in the BG conduit, we are measuring ~18V. When we trip the 400A feeder breaker feeding EVPNL-2 the voltage measurements goes away. When we pull the #3 AWG ground wire out of the conduit there is no damage to the wire, came out dry, and it pulled out easily. We made the ground connection by just running the ground wire laying on the asphalt and the noise on the signal wire went away.
We have a survey of existing underground utilities and the only other thing near our underground conduit run is a water line that runs parallel ~5ft away to a fire hydrant located near EVPNL-2.
So for some reason, when the ground wire is run in the conduit below grade we are getting a voltage induced on it and can't figure out why. Any ideas? Things we can test? Other things to check? We are all stumped...
We still want to megger the phase conductors in the conduits just to double check them, but I suspect they are fine.
Let me know if there are other details I can provide for additional clarity.
Here is our setup: We installed a 600A 208V panelboard "PNLBD-1" in a parking lot. It is fed from the building service entrance by parallel runs of 500KCMIL phase conductors and #3/0 AWG GND. The PNLBD-1 feeds two vendor specific 400A 208V EV panelboards "EVPNL-1" and "EVPNL-2" that have branch circuits out to EV chargers. The run between PNLBD-1 and EVPNL-1 is parallel runs each with #4/0 AWG phase conductors and #3 AWG GND (we were limited by lug size the vendor provided us on the EVPNL so had to run parallel sets...) and the same for EVPNL-2. The run to EVPNL-1 is <10ft above grade in a trough since they're located right next to each other. The run to EVPNL-2 is ~100ft underground. The EVPNLs have power conductors and a low voltage signal wires that run from each EVPNL out to the EV chargers.
Here is our problem: The low voltage signal wire is seeing noise on the signal that is causing issues with the EV chargers. We have traced it down to an issue with the ground in EVPNLs. After some investigations and lots of measurement with a multimeter focusing mostly on EVPNL-2, we have found a very odd problem - when we disconnect the #3 AWG ground wires (in the parallel run between PNLBD-1 and EVPNL-2) on both ends so that it is hanging free at both panels but still run in the conduit, we are measuring voltage (~9V) on it with reference to the ground bus/enclosure/AG conduit/etc in PNLBD-1 (one lead on the ground wire and one on the other objects). When we measure the voltage between both ground wires still hanging free on both ends and each in their individual run in the BG conduit, we are measuring ~18V. When we trip the 400A feeder breaker feeding EVPNL-2 the voltage measurements goes away. When we pull the #3 AWG ground wire out of the conduit there is no damage to the wire, came out dry, and it pulled out easily. We made the ground connection by just running the ground wire laying on the asphalt and the noise on the signal wire went away.
We have a survey of existing underground utilities and the only other thing near our underground conduit run is a water line that runs parallel ~5ft away to a fire hydrant located near EVPNL-2.
So for some reason, when the ground wire is run in the conduit below grade we are getting a voltage induced on it and can't figure out why. Any ideas? Things we can test? Other things to check? We are all stumped...
We still want to megger the phase conductors in the conduits just to double check them, but I suspect they are fine.
Let me know if there are other details I can provide for additional clarity.