D darekelec Senior Member Location nyc Yesterday at 9:28 PM #1 Does this car charger have a right to exist? It’s a pedestal charge point CT4000. Per manufacturer’s instructions provide 2 feeds of 40 amps each. Or should the installer provide a 4 pole disconnect ? Attachments IMG_5412.jpeg 122 KB · Views: 12
DBill64 Member Location Washington, USA Occupation I&E Technician Yesterday at 9:55 PM #2 What’s the single circuit wiring diagram on the next page look like?
qcroanoke Sometimes I don't know if I'm the boxer or the bag Location Roanoke, VA. Occupation Sorta retired........ Yesterday at 10:03 PM #3 No. Just 2-240 ckts. Charger has internal gfci protection. Are you asking if a disconnect is required at the chargers?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Yesterday at 10:04 PM #4 What's wrong with wiring as shown?
qcroanoke Sometimes I don't know if I'm the boxer or the bag Location Roanoke, VA. Occupation Sorta retired........ Yesterday at 10:04 PM #5 DBill64 said: What’s the single circuit wiring diagram on the next page look like? Click to expand... I looked at the manual. It requires a load sharing jumper I think. I didnt really look that hard.
tortuga Code Historian Location Oregon Occupation Electrical Design Yesterday at 10:05 PM #6 Looks to be 2 EVSE's in one pedestal
qcroanoke Sometimes I don't know if I'm the boxer or the bag Location Roanoke, VA. Occupation Sorta retired........ Yesterday at 10:07 PM #7 https://www.google.com/url?sa=t&source=web&rct=j&opi=89978449&url=https://www.chargepoint.com/files/CT4000_Install_Guide.pdf%3Fsrsltid%3DAfmBOoorKHwtxCCYkGR454EPPntr-Cj-2ihI4slOZmvlNtmcg-MKf4Oi&ved=2ahUKEwjq6KfboOyTAxVBMVkFHfB-Kb4QFnoECCQQAQ&usg=AOvVaw1lt1Xm7wSborWvGahC3Mfc Here's the manual