I have a job to bid:
Detached garage, residential.
Existing 1x 15A circuit
Add 60A EVSE
Looking here:
225.30 Number of Supplies.
A building or other structure that is served by a branch circuit or feeder on the load side of a service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (F).
A) Special Conditions.
Additional feeders or branch circuits shall be permitted to supply the following:
Would the resulting job be:
Run underground raceway to a switch/DC adjacent to existing circuit's then to evse. Ignore existing circuit otherwise. Check there is GEC for structure.
?
Or do I need to include existing circuit in raceway and repull to a subpanel?
Detached garage, residential.
Existing 1x 15A circuit
Add 60A EVSE
Looking here:
225.30 Number of Supplies.
A building or other structure that is served by a branch circuit or feeder on the load side of a service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (F).
A) Special Conditions.
Additional feeders or branch circuits shall be permitted to supply the following:
- (7)
Electric vehicle power transfer systems listed, labeled, and identified for more than a single branch circuit or feeder
Would the resulting job be:
Run underground raceway to a switch/DC adjacent to existing circuit's then to evse. Ignore existing circuit otherwise. Check there is GEC for structure.
?
Or do I need to include existing circuit in raceway and repull to a subpanel?