Electric-Light:
If all 0-10 dimmers have an internal voltage source, then what is used to control many fixtures as a group. I know ways to do it, but my question is what is normally done.
No, lighting dimmers do not have a voltage source. The dimming console is a variable load that sinks to a target voltage and the load applied is proportional to the number of fixtures. All the fixtures are connected in parallel and loaded down by a bus powered sinking voltage regulator. The number of fixtures allowed per control is limited by the sinking capacity of the control console.
The energy is dumped at the switch box. The sourcing capacity of each ballast is not allowed to be over 500uA and it is galvanically isolated from the power side to several thousand volts, as required by UL.
Some ballasts have a soft-off capability and might switch off under say 1v while some bottom out at the minimum dimming level. A short anywhere in the dimming circuit will pull everything to minimum or off state. This is why you need to ISOLATE the specific fixture and energize it with nothing connected to dimming wires. If the isolated fixture lights up, but everything else doesn't, the control wiring is crossed or shorted somewhere.
When you have violet and grey completely disconnected from suspected fixture and line voltage applied to white and black, but it still does not operate, then the driver/ballast/:lol: ED control box thingy is bad.
0-10v for THEATRICAL applications use a sourcing console and sinking luminaires. So, the dimming console needs a battery or an AC adapter to maintain galvanic isolation.