Ok, let's chase that rabbit hole.
725.130 Wiring Methods and Materials on
Load Side of the Class 2 or Class 3 Power
Source
Class 2 and Class 3 circuits on the load side of the power
source shall be permitted to be installed using wiring methods and materials in accordance with either 725.130(A) or (B).
(A) Class 1 Wiring Methods and Materials. Installation
shall be in accordance with 725.46.
Exception No. 2: Class 2 and Class 3 circuits shall be permitted
to be reclassified and installed as Class 1 circuits if
the Class 2 and Class 3 markings required in 725.124 are
eliminated and the entire circuit is installed using the wiring
methods and materials in accordance with Part II, Class 1
circuits.
725.49 Class 1 Circuit Conductors
.
(B) Insulation. Insulation on conductors shall be rated for
600 volts. Conductors larger than 16 AWG shall comply
with Article 310. Conductors in sizes 18 AWG and 16 AWG
shall be Type FFH-2, KF-2, KFF-2, PAF, PAFF, PF, PFF,
PGF, PGFF, PTF, PTFF, RFH-2, RFHH-2, RFHH-3, SF-2,
SFF-2, TF, TFF, TFFN, TFN, ZF, or ZFF. Conductors with
other types and thicknesses of insulation shall be permitted
if listed for Class 1 circuit use.
725.48 Conductors of Different Circuits in the
Same Cable, Cable Tray, Enclosure, or
Raceway
Class 1 circuits shall be permitted to be installed with other
circuits as specified in 725.48(A) and (B).
(B) Class 1 Circuits with Power-Supply Circuits. Class 1
circuits shall be permitted to be installed with power-supply
conductors as specified in 725.48(B)(1) through (B)(4).
(1) In a Cable, Enclosure, or Raceway. Class 1 circuits
and power-supply circuits shall be permitted to occupy the
same cable, enclosure, or raceway only where the equipment
powered is functionally associated.
This is where we need to apply some thinking, which really shouldn't be necessary if 725 were written clearly. We know that there is a luminary cable available with power and LV under one sheath. The manufacturer (AFC) spent a lot of money having this cable listed. Why would they do that if it were permissible to follow the Articles above and just use an off the shelf 4 conductor cable?
The answer is in the last sentence of 725.48(B)(1):
"Class 1 circuits and power-supply circuits shall be permitted to occupy the same cable, enclosure, or raceway only where the equipment powered is functionally associated."
As I remember, the phrase "functionally associated" is very strictly interpreted by the Code. There are rare instances where you can use it to reclassify a circuit. The NEC defines it to mean necessary for the operation of the equipment. One would think that you could run LV conductors to a condensing unit with the power if necessary. No, because the condensing unit doesn't need the thermostat in order to operate.
So, in our instance, can the luminaire operate without the LV dimmer? Yes it could. So dollars to donuts the NEC shot down allowing the 0-10V LV to be reclassified and be run with the power conductors because they didn't consider it functionally associated with the luminaires operation.
-Hal