david
Senior Member
- Location
- Pennsylvania
So, in our instance, can the luminaire operate without the LV dimmer? Yes it could. So dollars to donuts the NEC shot down allowing the 0-10V LV to be reclassified and be run with the power conductors because they didn't consider it functionally associated with the luminaires operation.
-Hal
I do not think that is the threshold at all, it isn’t that the fixture can operate without a dimming function.
The threshold would be when you are using a dimming function are the power cables and low voltage circuit functionally associated.
Lets say you have multible 0-10 volt dimmers ganged in one location. Three on the left and three on the right same switch box.
There is one 20 amp branch circuit for the fixtures. There is a pull box in the ceiling that you intend to go left and right in the building to control lighting fixtures.
You run one conduit from the pull box to the switch box in the conduit you have the 0-10 volt class 2 circuits and the 20 amp branch circuit you need to reclassify the class 2 circuits ,
the 20 amp branch circuit and the original class 2 circuits are functionally associated with dimming the lighting fixtures.
However same exact circumstance as sated except you feed the switch box with two 20 amp branch circuits one for half the fixtures being dimmed and one 20 amp branch circuit for the other three dimmers being used to control dimming of the fixtures.
If you use one pull box in the ceiling and one conduit to the switch box it could be stated that one of the 20 amp branch circuits is not functionally associated with three of the 0-10 volt dimmers controlling half of the fixtures being dimmed.