A Alwayslearningelec Senior Member Location NJ Occupation Estimator Sep 15, 2025 #1 Would need to use this in my application. Thought per code it would not be more than 6'? 12-2 SOL CU THHN MC-PCS EZ QUICK WHIP BLACK/WHITE/GREEN 16/2 AIA 10' 45EA | Southwire www.southwire.com
Would need to use this in my application. Thought per code it would not be more than 6'? 12-2 SOL CU THHN MC-PCS EZ QUICK WHIP BLACK/WHITE/GREEN 16/2 AIA 10' 45EA | Southwire www.southwire.com
S Strathead Senior Member Location Ocala, Florida, USA Occupation Electrician/Estimator/Project Manager/Superintendent Sep 15, 2025 #2 IF you used this you would need to strap it. So it seems this wouldn't be a good solution for a typical fixture whip.
IF you used this you would need to strap it. So it seems this wouldn't be a good solution for a typical fixture whip.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Sep 15, 2025 #3 Alwayslearningelec said: Would need to use this in my application. Thought per code it would not be more than 6'? Click to expand... The 6' limit would not apply to that whip because it's #12 MC cable.
Alwayslearningelec said: Would need to use this in my application. Thought per code it would not be more than 6'? Click to expand... The 6' limit would not apply to that whip because it's #12 MC cable.