I am in Seattle and read a inspecters ding page that pointed it out in the NEC that said 15' spacificlly.I cant find that spacific stating 15' is it there?
I know the Washington Admistration Code (WAC, State electrical code) it says 15' feet found in WAC 296-46B-230-070-(11)(b). The city of Seattle may have adopted the States requirement in this case.
Seattle Electrical Code said:230.70 General. Means shall be provided to disconnect all
conductors in a building or other structure from the serviceentrance
conductors.
(A) Location. The service disconnecting means shall be
installed in accordance with 230.70(A)(1), (A)(2), ((and))
(A)(3) and (A)(4).
(1) Readily Accessible Location. The service disconnecting
means shall be installed at a readily accessible location either
outside of a building or structure or inside nearest the point
of entrance of the service conductors. Service disconnecting
means shall be readily accessible, including after any
subsequent building alterations or additions.
FPN: The inside and outside location requirements
contained in WAC 296-46B-230.070(11) are by this
reference made part of the 2008 Seattle Electrical Code.