If you are in San Francisco here is the link to the electrical requirements.
http://www.amlegal.com/library/ca/sanfrancisco.shtml
Gosh I've been bonding around gas water heaters for 30 years
Even tho I thought it was dumb cause the water heater tied them all together...
And it wasnt even needed!?:slaphead:
And I'll do it again on Monday!
So the gas Pipe on the water heater has to be bonded or not?
Is it bonded with a jumper
Or grounded with the gec?
I believe it needed the same size ground as the service so gec
If you are installing this bond at the water heater to bond hot and cold I must ask where in 250.104 it allows a metal water pipe to be bonded to another metal water pipe.
250.104(A)(1) allows the metal water pipe to be bonded to four places and I can?t find a water pipe listed. Could you show me where?
Updates
Inspector says no PVC allowed for grounding wire.
She would rather see stranded wire bigger than #4
Updates
So now I only have to run a #3 for the gas bond
It is 50'. To the main and only 8' to the water entrance
Can I split bolt or clamshell the #3 to the 1/0
Or do I have to run to the disconnect?
Also the disconnect is all one piece with the meter base
Can I just land anywhere in the enclosure?
And finally, the ground rod is not anywhere visible
Should I just drive one and land 1/0 even though
She didn't write it up?
Updates
Run loose if strapped with listed strap.
On her insp report she wanted the cold water bond
which I uncovered at the entrance
And the gas bonding. I asked her if the gas bond had
To be the same 1/0 as the gec and she said no, much smaller
She didn't write it up? This install was just green tagged
By the city in 2006 and she thinks it must have been
Good then, but that the wires "may have been removed"
Client thinks there's a certain corruption or
Good old boy because they paid for and got signed off on
A garage fire sprinkler system which was never installed
Thx
If the water heater is installed with dielectric unions, then a jumper must be installed to make the piping system "an effective grounding path"
(1) Continuity. Continuity of the grounding path or the bonding connection to interior piping shall not rely on water meters or filtering devices and similar equipment.
Be advised, you enter this debate with Mike at your own risk, he has made his view pretty clear on this forum more than once of what is a metal piping system and what needs bonded more than once - I can't really disagree with most of what he has said.![]()
The section of the NEC you have quoted above has nothing to do with 250.104(A)(1) but instead it concerns the first five feet where we are allowed to land the GEC to the underground electrode and also use this same GEC to do the bonding to the interior metal pipe as required in 250.104(A)(1). The section you have posted is the 250.104(A)(1) bond back to the electrode.If the water heater is installed with dielectric unions, then a jumper must be installed to make the piping system "an effective grounding path"(1) Continuity. Continuity of the grounding path or the bonding connection to interior piping shall not rely on water meters or filtering devices and similar equipment.If you are installing this bond at the water heater to bond hot and cold I must ask where in 250.104 it allows a metal water pipe to be bonded to another metal water pipe. 250.104(A)(1) allows the metal water pipe to be bonded to four places and I can?t find a water pipe listed. Could you show me where?
If the water heater is installed using non-metallic pipes the requirement found in 250.104(A)(1) does not change in any way.
If you believe that the use of non-metallic fittings or stubs at a water heater in some way causes a separate bonding for the other water pipe then this other water pipe must be bonded as outlined in 250.104(A)(1) and I can?t find where this other metal water pipe is allowed to be installed from one pipe to another.
What would you consider the purpose or intent of 250.104 to be?
No I am not repeating myself. You said that, ?If the water heater is installed with dielectric unions, then a jumper must be installed to make the piping system "an effective grounding path" and then quoted the code section concerning bonding the 250.104(A)(1) to the 250.52(A)(1) electrode, ?(1) Continuity. Continuity of the grounding path or the bonding connection to interior piping shall not rely on water meters or filtering devices and similar equipment.?Mike you keep repeating yourself. The conection points for termination are correct.
What is being bonded and terminated at these 4 locations?
Can't help my self so here goesMike you keep repeating yourself. The conection points for termination are correct.
A wire? Did I get it right? :lol:
Perhaps one of the moderators would make this its own thread starting with post # 22, this could take a while.
The interior water piping system is what is being bonded, and is being terminated at one of the 4 mentioned locations with a bonding jumper.
Exactly and the following statement is not part of anything that can be found in the NEC anywhere. The following is nothing more than a wives taleThe interior water piping system is what is being bonded, and is being terminated at one of the 4 mentioned locations with a bonding jumper.