LOL... I also edited my post and added a bit of commentary
Yeah I saw that, I ignored it since it just shoots more holes in my losing argument.
LOL... I also edited my post and added a bit of commentary
Ahhh you learned well my son. Ignore what shoots holes and you save face... :lol:Yeah I saw that, I ignored it since it just shoots more holes in my losing argument.
The entire 338.10(B) vs 310.15(2), (B)(6) has been so confusing since day 1 it is little doubt the CMP members disagree.
We are not on the '14 Code but I'm told it does little to clarify the situation.
It's a shame the CMPs can't develop a simple, easy to understand solution
Originally Posted by jumper View Post
Is Dave Mercier a CMP member or IAEI or just works at Southwire? Just curious.
Dennis Alwon said:CMP and it was he who got the seu dropped to 60C. Apparently his company (southwire) did a study on the cables in firecaulking and said under full load the wire was breaking down. Now we all know that you never have seu under full load especially in a residence.
Actually I find 310.15(B)(7) easy to follow now. It finally made it clear that corrections and adjustments do apply. The issue of applying 310.15(A)(2) where applicable to SE cable is in my mind clear....since it does not exclude 310.15(A)(2) like it does in 334.80 then it can be applied. As for Dave, he is on that CMP but obviously he did not voice his facts during that process because as you can see another CMP member and IAEI representative on that panel gives a different view. Also all articles for submission are reviewed by multiple sources and did not object.
Interesting. I wonder why he never responded to me when I questioned him on that. I guess he realized he was incorrect-- IDK
So, the answer to the OP is ???
Wow! I wish I could learn to hush when I'm incorrect
So, the answer to the OP is ???
IMO the answer would depend on how much insulation the ser is passing thru. If it is more than 10' or where 310.15(A)(2) does not apply then 60C would be the temp. rating. If it is just caulking then 75C would rule.
This is what I was taught and at first I agreed with you but after reading this thread I have officially changed my mind to 310.15(A)(2) applies... Now the real question is what will the local ahj think since his onion is all that matters in the end.Only one problem, 310.15(A)(2) ain't gonna work for SER in thermal insulation. You only have one final ampacity. No portion is higher or lessor. The 60C does not just apply to the portion in the insulation.
This is what I was taught and at first I agreed with you but after reading this thread I have officially changed my mind to 310.15(A)(2) applies... Now the real question is what will the local ahj think since his onion is all that matters in the end.
So if I understand this correctly, one could run SER attached to the underside of the roof framing where there is no insulation, (or have a means for the cable to be kept out of insulation, but maintain supports @ 4 1/2'), except where you run down the wall to the main or sub-panel, and be able to use the 75 degree rating?
So if I understand this correctly, one could run SER attached to the underside of the roof framing where there is no insulation, (or have a means for the cable to be kept out of insulation, but maintain supports @ 4 1/2'), except where you run down the wall to the main or sub-panel, and be able to use the 75 degree rating?
Always read about the product that you are using.
"60?C - When terminated to equipment for circuits rated 100 amperes or less or marked for 14 through 1 AWG conductors."
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheetOEM46