And why is pulling 9 wires is a resi. different than pulling 9 in a comm. applicaton?
No different except more likely to have that many ccts heading in the same direction for any distance in commercial (Mcmansion excluded). IMO by the time you install 9 wires & sort through the colors & the grand plan you could have run 2-3 homeruns in 1/2". I see whole houses w/o 1 stick of 3/4".
You'd better watch it, he's got a bigger sparky number than you !!!!! Sorry, Im falling out of my chair laughing !! couldnt resist....forgive me...!!!![]()
Ok Im sorry,:smile: Ive probably offended 480sparky
How many wires do you plan on running in the future in this 3/4" EMT?
You can run twelve 14 ga or nine 12 ga THHN wires in 1/2" EMT. Any more than nine current-carrying conductors in any size conduit has to be derated.
When you bend 1/2" EMT it doesn't stay put? LMAO!
When did more than Three Current Carrying Conductors not be required derating?
So if you needed to run 9 wires, you'd rather run two or thee 1/2"s? I'd fire someone who did that on a consistent basis
Thousands & thousands of homes in EMT in this area. No NM, No 3/4" EMT.
totaly Nieve on my part, I did not realize that there were homes being wired in EMT. My post question was aimed at commercial
They are derated. But you derate using the ampacity of T310.16. Circuits using 14, 12 and 10 can be derated up to 9 conductors and still not be below the maximum OCPD specified in 240.4(D).
In other words, nine #12 THHNs have an ampacity of 21 amps (30*0.7). So you still can use a 20a breaker.
You can run twelve 14 ga or nine 12 ga THHN wires in 1/2" EMT. Any more than nine current-carrying conductors in any size conduit has to be derated. ...
Who would run nine wires in any size conduit(res)? A waste of time IMO.
Thousands & thousands of homes in EMT in this area. No NM, No 3/4" EMT.
From a fire code stand point, I figure that as the density of homes and people tightens up closer and closer, it comes to the point that the risk of loosing several homes from one fire makes them require conduit installations over romex....
They run the EMT in wood framed homes, I don't see the benefit. :smile:
The only benefit that I can see is being able to add more circuits down the road. But that can easily be done with ENT/"smurf tube" faster and cheaper than EMT.
I was replying about the fire prevention angle. :smile: