hotel. What would conduit/wire combo would give one hour rating.
EM feeders need extra protection per 700.10(D). A method that provides one hour protection is not acceptable.
(D) Fire Protection. Emergency systems shall meet the additional
requirements in (D)(1) through (D)(3) in the following
occupancies:
(1) Assembly occupancies for not less than 1000 persons
(2) Buildings above 23 m (75 ft) in height
(3) Health care occupancies where persons are not capable
of self preservation
(4) Educational occupancies with more than 300 occupants
(1) Feeder-Circuit Wiring. Feeder-circuit wiring shall meet
one of the following conditions:
(1) The cable or raceway is installed in spaces or areas that
are fully protected by an approved automatic fire suppression
system.
(2) The cable or raceway is protected by a listed electrical
circuit protective system with a minimum 2-hour fire
rating.
Informational Note No. 1: Electrical circuit protective systems
could include but not be limited to thermal barriers or a protective
shaft and are tested to UL 1724, Fire Tests for Electrical Circuit
Protection Systems.
Informational Note No. 2: The listing organization provides
information for electrical circuit protective systems on proper
installation requirements to maintain the fire rating.
(3) The cable or raceway is a listed fire-resistive cable system.
Informational Note No. 1: Fire-resistive cables are tested to
ANSI/UL 2196, Tests for Fire Resistive Cables.
Informational Note No. 2: The listing organization provides
information for fire-resistive cable systems on proper installation
requirements to maintain the fire rating.
(4) The cable or raceway is protected by a listed fire-rated
assembly that has a minimum fire rating of 2 hours and
contains only emergency circuits.
(5) The cable or raceway is encased in a minimum of 50 mm
(2 in.) of concrete.