We have (14) sunny boy tl us single phase inverters,the original plans called for 3 phase inverters long story, but they got changed to single phase (note) this is a 208 3 phase grid.the original plans called for a 10amp 3 phase breaker for each of the 14 inverter never seen a 10 amp CKT breaker we just put 15 amp with 10 AWG wire , we jumped the gun and did not wait for the changed plans. new plans are calling for 40 amp 8 AWG wire for each inverter. Inverters will be drawing 28.8 amps X1.25 = 36. We already passed inspection with the single phase inverters with the original approved set of plans containing the 3 phase inverters, I'm thinking the inverters will never draw the max amps and if it did it would not be for very long, would it be a safety issue if I just put 30 amp ocpd for each inverter and not multiply by 1.25 thank you