I don't think you made the exception of using a RMC nipple in this case.
Put it this way I don't think the code intended for multiply nipples. While it may be a nipple, in thought, but it's still a raceway.
Not sure what you're trying to say. Yes, it's still a raceway, and is allowed to be filled to 60%. 3#1+1#6 THHN would have an area of 0.5193 sq. in. The 1" rigid would have an allowable fill of 0.532 sq. in. The conductors fit the fill requirements.
If they cut the conduits at floor level they would not make the exception of 250.86 Exc #2 cause they don't know how it's attached.
If they they leave some conduit can one put a hogs head on it, or a thread-less coupling, your box and a bonding bushen, and do as you imply?
I'm not suggesting he cut the conduit flush to the floor, just that he cut the length to 24". He noted a 12" attic floor depth, so he'd have 6" to work with at both ends.