1 neutral conductor per terminal, code section help

Status
Not open for further replies.

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
I am having brain fade, I know in a panel we can put 2 ground conductors under one lug if the manufacturer lists it that way. I know we can't put 2 neutrals/grounded conductors under one lug, but I can't find the code section. Also would this apply to a large lug that is made for multiple parallel conductors (1/0 or larger) installed by the manufacturer.
 

iwire

Moderator
Staff member
Location
Massachusetts
408.41 Grounded Conductor Terminations. Each
grounded conductor shall terminate within the panelboard
in an individual terminal that is not also used for another
conductor.

Exception: Grounded conductors of circuits with parallel
conductors shall be permitted to terminate in a single terminal
if the terminal is identified for connection of more
than one conductor.
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
Thanks, that was FAST. I thought it was ok for parallel conductors.
 

jetlag

Senior Member
408.41 Grounded Conductor Terminations. Each
grounded conductor shall terminate within the panelboard
in an individual terminal that is not also used for another
conductor.

Exception: Grounded conductors of circuits with parallel
conductors shall be permitted to terminate in a single terminal
if the terminal is identified for connection of more
than one conductor.

Thats good cigar for you
 