Can I use a 208V, 3-ph power supply to feed a 1-ph 230V AC unit? this is the European style one hot and one neutral AC unit.
I would not do it without authorization from the manufacturer.Can I use a 208V, 3-ph power supply to feed a 1-ph 230V AC unit? this is the European style one hot and one neutral AC unit.
If it is European then it will be 50Hz, not 60Hz.Can I use a 208V, 3-ph power supply to feed a 1-ph 230V AC unit? this is the European style one hot and one neutral AC unit.
Do you have a manual? Does it say you can do this? presumably you want to power it from two of the 208 V lines.Can I use a 208V, 3-ph power supply to feed a 1-ph 230V AC unit? this is the European style one hot and one neutral AC unit.
If it were made in the US with US motors 10HP and under, the motor would most likely be rated for use at 208 or 230V. But IEC motors are marginal to begin with (i.e. no Service Factor), so running an IEC 230V motor at 208V would likely result in premature failure. I would get the buck-boost transformer as Bob suggested.Can I use a 208V, 3-ph power supply to feed a 1-ph 230V AC unit? this is the European style one hot and one neutral AC unit.