- Occupation
- Licensed Electrician
If everything is connected properly the fault current path will include the GEC and the earth as a by-product but the majority of the fault will be flowing through the effective ground fault current path and straight to the secondary without even noticing if there is a GEC or not.I understand what the GEC does. I was thinking in having one on a SDS could shorten the fault current path for a fault on the secondary, depending on where the fault occurs. Is that incorrect?