Discovered someone installed a 1-Phase 120V/ 240V/ 1Ph/ 3W/ G
load center on secondary of a 480V Delta to 208Y/ 120V/ 3Ph/ 4Wire dry-type general use transformer. This is all new work & is the only item on the transformer secondary. Do not yet know the loads or details. Is this a code violation?
It does not make a lot of sense - why buy 3-Phase transformer to serve 1-Phase load? Will load imbalance create voltage imbalance?
Thanks