The contractor I work for installs a lot of UPS and generator systems. One UPS we install is a small (typical 12 kVA) name brand single phase unit. The output voltages are:
L1-N 120V L2-L3 208V
L2-N 88V L1-L2 32V
L3-N 120V L1-L3 240V
The output can be configured either 120/208 or 120/240. They specify using a 3 phase panel for the 120/208 single phase configuration. What does the NEC say concerning using a 3 phase panel for this? I don't agree with having 88V on L2 even if the panel is marked as such. Why not use a single phase panel instead?
Also, when does the code require an EPO (E-Stop) button for a UPS? What is considered an information technology room? We usually err on the side of caution, and install one.
Bryan
L1-N 120V L2-L3 208V
L2-N 88V L1-L2 32V
L3-N 120V L1-L3 240V
The output can be configured either 120/208 or 120/240. They specify using a 3 phase panel for the 120/208 single phase configuration. What does the NEC say concerning using a 3 phase panel for this? I don't agree with having 88V on L2 even if the panel is marked as such. Why not use a single phase panel instead?