How to safely have 1 portable generator feed 2 200 Amp panels with generator interlock. Addressing isolating grounded conductor between panels.
Scratch that. After thinking about it you couldn't feed It back onto the grid.Switching it correctly to not backfeed onto the grid would concern me more than neutral currents
SDS, actually the correct way of doing it.why are you sending the neutral thru the contactor ?
True but a great percentage of generator installs that size are not SDSSDS, actually the correct way of doing it.
And the utility neutral is still connected even when genset is running. I see no reason to use a contactor.True but a great percentage of generator installs that size are not SDS
True but a great percentage of generator installs that size are not SDS
You still have a small neutral from the generator paralleled with the larger panel neutrals, but usually is a non issue on that small of a service. As you said, a vast majority of the installations are that way. Just technically not right.And the utility neutral is still connected even when genset is running. I see no reason to use a contactor.
Notice this post is AI generated. How the generator is bonded and grounded is determined by the transfer switchHere's how to safely have 1 portable generator feed 2, 200 Amp panels with a generator interlock, addressing the isolation of the grounded conductor between panels:
Important Disclaimer: Electrical work, especially involving generator installations and modifications to electrical panels, can be dangerous if not done correctly. This information is for informational purposes only and should not be a substitute for consulting with a qualified electrician who can assess your specific situation and ensure safe and code-compliant installation.
Generator Requirements:
Addressing Isolation of Grounded Conductor:
- Size: The generator needs to be adequately sized to handle the combined load of both 200 Amp panels. Determine the total wattage or amperage of all appliances and equipment you plan to power simultaneously across both panels. Choose a generator with a continuous output rating that exceeds this total by 20-30% to account for starting surges.
- Transfer Switch or Interlock Kit: A transfer switch or interlock kit is crucial to prevent accidentally backfeeding power to the utility grid. This ensures your home's electrical system is completely isolated from the utility while operating on generator power.
Here's the key point regarding the grounded conductor:
Here's a breakdown of the installation process (refer to a qualified electrician for actual work):
- In the United States (NEC standards): The 2023 National Electrical Code (NEC) typically requires a 4-wire transfer switch for generator installations with a separate neutral and grounding conductor. This ensures the neutral and grounding conductors remain isolated between the generator and utility supply.
Additional Considerations:
- Identify Panel Types: Determine if your existing panels are main breaker panels or subpanels. This will influence the specific installation approach.
- Install Transfer Switch: Install a 4-wire transfer switch with a capacity exceeding the generator's output rating. The transfer switch will be connected to the utility feed, generator output, and the two 200 Amp panels.
- Isolating Grounded Conductor: During the transfer switch installation, ensure the grounded conductor (neutral wire) coming from the generator is isolated from the grounded conductor of the utility feed. The transfer switch should have separate terminals for the neutral and grounding conductors from both sources.
- Panel Bonding: The grounding conductor from the generator will connect to the grounding bus bar in the transfer switch. In most cases, the neutral conductor from the generator should not be connected to the grounding bus bar or any other equipment grounding conductors within the transfer system. Consult a qualified electrician for specific bonding requirements based on your panel types and local codes.
- Interlock Kit (Alternative): If using an interlock kit instead of a transfer switch, ensure it's a 4-wire kit designed to isolate the neutral conductor. However, transfer switches are generally considered a safer and more reliable option for generator installations.
Remember, safety is paramount when dealing with electrical wiring and generators. Don't attempt any electrical work yourself unless you are a qualified electrician.
- Permit Requirements: In many areas, permits are required for installing a generator and modifying electrical panels. Check with your local building department to understand the permitting process.
- Qualified Electrician: While this information provides a general overview, it's highly recommended to consult with a qualified electrician to ensure a safe and code-compliant installation that meets your specific needs and local regulations. They can assess your existing electrical system, select the appropriate transfer switch or interlock kit, and perform the installation according to best practices.
Do you think Ruxton is AI?Notice this post is AI generated. How the generator is bonded and grounded is determined by the transfer switch
Step 5 says to use a 4 wire interlock kit..... I don't think I've ever seen one of those.....Notice this post is AI generated. How the generator is bonded and grounded is determined by the transfer switch
I had an AI response to a question for a mini split, the seller did not list the amps, only volts, and btu. Instead of answering the question, it said that information was not specified, and to call the manufacturer. Duh! The seller should have this info if they want to sell it. BTU’s mean nothing to an electrician!Notice this post is AI generated. How the generator is bonded and grounded is determined by the transfer switch
This post covers generator installations with a separate neutral and grounding conductor, as previously mentioned.Notice this post is AI generated. How the generator is bonded and grounded is determined by the transfer switch
It is like the kits that you see at Costco every now and then.Step 5 says to use a 4 wire interlock kit..... I don't think I've ever seen one of those.....
I am sorry for your bad experience with AI! Sometimes, that is the best it can do - it's not a magic bullet. It is for sure not possible to guess the ampacity from BTU alone, only to get a general idea of course (e.g. NN A or NNN A).I had an AI response to a question for a mini split, the seller did not list the amps, only volts, and btu. Instead of answering the question, it said that information was not specified, and to call the manufacturer. Duh! The seller should have this info if they want to sell it. BTU’s mean nothing to an electrician!