Jim W in Tampa
Senior Member
- Location
- Tampa Florida
A/C unit says min circuit amps 32 min. breaker 50 amps ,is this reall safe on #10 thhn ?
Jim W in Tampa said:A/C unit says min circuit amps 32 min. breaker 50 amps ,is this reall safe on #10 thhn ?
1793 said:Table 310.16 For #10 THHN 75d* is 35 amps. *240.4(D). #10-30 amps
If you use 10-2(Romex) then you would have to use the 60d rating of 30amps.
You stated 32 amp min. so as I see it you can not use 10-2.
I'm sure if I'm wrong someone will let me know.
Jim W in Tampa said:Is my thhn not ok to carry 35 amps ?My concern is the 50 amp breaker,really dont like it being that high.
The "*" refers you to 240.4D which refers to 240.4E thru 240.4G. 240.4G1793 said:I would tend to agree that if you used THHN then the 35 amps could be used, however I keep looking at the " * " that sends us back to 24.4(D) #10-30 amps.
infinity said:240.4(d) does not apply to AC units that fall under article 440. Your #10 THHN (75 degrees C=35 amps) may be used for this application however if you used NM cable than it's ampacity is limited to the 60 degree C column of 310.16 which is an ampacity of 30 amps. Therefore if using NM you would need #8-2 NM cable.
bob said:The "*" refers you to 240.4D which refers to 240.4E thru 240.4G. 240.4G
references table 240.4G. In this table section 440 allows the over current device to be 175% of the FLA of the A/C unit.
steve66 said:I thought this would be easy, but I'm not sure. 240.4(D) says #10 can only be used with breakers up to 30A unless "specifically" permitted in 240.4E or G. Although 240.4(G) refers to article 440, I don't see anything in 440 that "specifically" says #10 can be used at 50A.
My guess is that #8 is required.
Steve
steve66 said:I thought this would be easy, but I'm not sure. 240.4(D) says #10 can only be used with breakers up to 30A unless "specifically" permitted in 240.4E or G. Although 240.4(G) refers to article 440, I don't see anything in 440 that "specifically" says #10 can be used at 50A.
My guess is that #8 is required.
Steve
infinity said:I would disagree. What is the ampacity of #10 THHN?
Answer is 40 amps.
For other then derating can we use the 40 amp rating?
No, because we know that the terminations that we use are rated for 60 or 75 degrees, so the ampacity is limited to either the 60 or 75 degree rating.
Furthermore 240.4(d) reduces the ampacity to 30 amps unless it is used for equipment covered under Article 440. Since an AC unit is covered under article 440, 240.4(d) does not apply.
1793 said:So are you saying that we can load the #10 to the 35 amps(310.16 75d)
ryan_618 said:Guys, we are talking about romex, therefore 334.80 limits us to the 60 degree column. 8 AWG required.
jcole said:Or am I missing something in 440 that overrides this general rule?
Jim W in Tampa said:You have a good point.I am assuming my CH breaker and pullout disc.are 75