10-amp and 6.25-amp plug fuses

Status
Not open for further replies.

jeff48356

Senior Member
I remember back when I was a boy, the local hardware store sold 10-amp and 6.25-amp plug fuses. I've always wondered what they would possibly be used for, since the minimum amperage of a branch circuit is 15 amps. Were these used in those fused switches for controlling individual motors? That's the only thing I can think of. Anyone have any experience with these?
 
I’ve seen low amperage plug fuses mounted with a switch on the circuit feeding a gas furnace. Usually mounted right in the furnace.
 
Another one - my daughter bought a house that had an old GE electric range in the basement. It had a 120 V convenience receptacle built into the back panel. It had a plug fuse to protect it - I think it was a 10 A.
 
I remember back when I was a boy, the local hardware store sold 10-amp and 6.25-amp plug fuses. I've always wondered what they would possibly be used for, since the minimum amperage of a branch circuit is 15 amps. Were these used in those fused switches for controlling individual motors? That's the only thing I can think of. Anyone have any experience with these?
Branch circuits in general the minimum conductor size permitted is 14 AWG - which is protected by a 15 amp OCPD.

There is a need for less then 15 amp devices for control circuits using 16 or 18 AWG conductors.

You can also use a fuse for motor overload protection.

A 6.25 amp time delay fuse is perfect for a 5 amp motor with 125% overload protection.
 