Is anyone who is under the 2023 NEC using 10 amp lighting circuits with #14 copper clad aluminum wire?
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Does anyone make #14 CCA building wire?
Does anyone make connectors listed for CCA building wire?
Does anyone make 10 amp AFCI breakers (dwelling use)?
 

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
Does anyone make #14 CCA building wire?
Does anyone make connectors listed for CCA building wire?
Does anyone make 10 amp AFCI breakers (dwelling use)?
Copper weld makes it.
I got some at my shop. Did not price out any different than copper.
Less cost in materials vs more in labor cause of box fill and pig tailing all 10-2 copper clad to 12-2 copper for devices was a pain. Not worth it.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Copper weld makes it.
I got some at my shop. Did not price out any different than copper.
Less cost in materials vs more in labor cause of box fill and pig tailing all 10-2 copper clad to 12-2 copper for devices was a pain. Not worth it.
The smallest size I see on their web site is #12.

Even in the larger 12 & 10 AWG sizes how do you pigatail? I have not seen any standard "wire nut type" connectors that are listed for other than CU only.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
In theory, it seems the copper cladding should make it compatible with CU-rated splices and terminations.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
There are no OCPDs marked as required by 240.4(D)(3)(a) or (b), so there is no way to use 14 AWG CCA at this time.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Forget aluminum I was hoping they would open up it to 16 AWG romex. People have been using it on boats for years as 10 Amp lighting circuits.
This is 16/3 AWG UL 1426 Flat Marine Wire - Tinned Copper Boat Cable: