#10 awg ground tails

Status
Not open for further replies.

JoeHon

Member
Location
Chaska, MN
We are installing 50 amp devices. I believe my #10 EGC has to extend to the device, but does my pig tail also have to be #10? 250-122 leads me to believe that it does, but I am having trouble locating this product at a supply house which leads me to believe I may be missing something? Thanks for your help.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Why not just make them with a ground screw and piece of # 10?

Roger
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you are using So cord then generally the equipment grounding conductor is the same size as the other conductors. 250-122 does allow a #10 to be used as the equipment grounding conductor but as I stated I don't think you will find a #8 So xx cord with a #10 equipment grounding conductor.
 

JoeHon

Member
Location
Chaska, MN
Please allow me to clarify a little more. This is a data center enviroment, we are using 8/3 w/ ground cora clad and running to a metal box with a 2 wire 50A device that computer equipment plugs into. The 8/3 has a #8 ground which is oversized since we are using a 50 amp overcurrent protection device. I believe the code (250-122) requires me to run at least #10 to the device, my primary concern is the pig tail to the box and the sizing requirements. I believe it falls under 250-122 as well??

Roger- Thank you I believe that may be what we have to do. And thanks to everyone for your feedback, this seems to be a great forum.

Joe
 

eHunter

Senior Member
Please allow me to clarify a little more. This is a data center enviroment, we are using 8/3 w/ ground cora clad and running to a metal box with a 2 wire 50A device that computer equipment plugs into. The 8/3 has a #8 ground which is oversized since we are using a 50 amp overcurrent protection device. I believe the code (250-122) requires me to run at least #10 to the device, my primary concern is the pig tail to the box and the sizing requirements. I believe it falls under 250-122 as well??

Roger- Thank you I believe that may be what we have to do. And thanks to everyone for your feedback, this seems to be a great forum.

Joe

Take a look at:
http://www.ebay.com/itm/Green-Groun...6-inch-Stranded-Wire-/150557311514#vi-content
 

kwired

Electron manager
Location
NE Nebraska
Wouldn't that be dependent on the type of box?
beyond the box being metallic (which I mentioned) what else did you have in mind?

The device must have its mounting yoke/strap be metallic and connected to equipment grounding conductor terminal of receptacle devices also, but I don't think you will find any that are not.

Flush devices that do not make metal to metal contact must have a bonding jumper, but that is covered in what I said before.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Flush devices that do not make metal to metal contact must have a bonding jumper, but that is covered in what I said before.

I was thinking of flush devices that do make metal to metal contact with the yoke or an old work (gem) box.
 