Someone told me that you could not derate #10 ground. Can you derate #10 ground from #10 to #12?? Please give the code reference for this
No idea of what anyone is talking about when they use the undefined term of "ground". The understanding of Articles 200 and 250 is generally poor and terms are often used outside of how they are used in the code.He asking if you can use a smaller EGC when the circuit conductor is a #10 AWG.
Answer: no, 250.122(B).
Agree. Mike Holt once saidNo idea of what anyone is talking about when they use the undefined term of "ground". The understanding of Articles 200 and 250 is generally poor and terms are often used outside of how they are used in the code.