Carultch
Senior Member
- Location
- Massachusetts
Grounding electrodes are not about clearing faults. If a rod is the only available electrode doesn't matter if you have 100 amps of service or 4000 amps of service, that rod (plus a supplemental rod if you don't want to measure resistance) is good enough for either application as a grounding elecrode.
An acceptable 25 ohm rod installation will not let enough current flow to even trip a 15 amp breaker. Even @ 277 volts the 25 ohm rod only lets about 11 amps of current flow.
Ok, that makes sense.
So to summarize:
The ohms of the ground rod system is all that ultimately matters in any application, and in most cases you achieve it with two ground rods at min 8 ft embedment and the standard 6 ft separation.