It never was an exception in the first place. It was a method of complying with the 2014 version of the rule. The rapid shutdown doesn't cease to exist, you just wouldn't need rapid shutdown specific equipment to comply (like a contactor or shunt trip combiner at the time). The rapid shutdown rule would only cease to exist, if your system never touched a building.
The working principles behind a inverter operation, would allow the entire the entire AC side to de-energize upon opening the master switch, and therefore the DC side that remained energized would have to remain within the array + 10 ft offset. The current rule in NEC2017 and NEC2020 no longer allows "combiner level shutdown"/"inverter level shutdown" like this. It tightens the boundary to a 1 ft offset, outside which 30V is the maximum, and requires max 80V within the array. Practically, this means module-level shutdown, since a typical module in open circuit is between 40 and 80V. With most modules, the most you could combine prior to a rapid shutdown device is parallel combinations of individual modules, since 2 in series usually exceeds 80V.