ChillSparky
Member
- Location
- Golden, Colorado, USA
What I have is a 3 Phase Delta 208V 200 Amp Disconnect after a meter. The Disconnect originally and still does feed a 200A Cutler Hammer panel directly behind it inside of the building. We were hooking up a rather large cooler with max OCP of 90A. Just to the left of the first disconnect (the one feeding the inside panel) we set a 100A fusible disconnect with a set of 90A fuses. This is approximately 6 ft from lug to lug for the conductor length. In order to comply with the 10ft tap rule, what side of the 200A Disco can we tap from? And why would an inspector require us to match the conductor size that serves the 200A Disco? I believe we had #4 feeding the 90A, which is within the 1/10th of the conductor size 3/0. I'm confused as to how and when 240.21 can be applied. Thanks in advanced guys!!