if im tapping off of a set of 500's to feed a 150 amp panel would i be able to use #1's in the 90 degree column to feed the panel since i dont have a breaker directly protecting these conductors?
NEC 240.21 (B)(1) says nothing about terminating on an ocpd, the panel is protected by the breaker feeding the 500's, why would the temperature rating of the lugs matter on the main lug panel 150 amps is a 150 amps the maximum wire rating is still equal to the lugs
The tap conductor is rated for 130 amps. What will protect those conductors from overcurrent, the OCPD ahead of the 500 kcmil conductors?
The UL listing for panelboard (QEUY) states that panelboard terminations are listed for 60? for wire sizes 14-1 unless otherwise marked.
So it would seem your #1 is limited to 110 amps unless the panelboard is marked otherwise.
yes................
My opinion is that the 10 ft tap rule is one (maybe the only one) that does not specifically state terminate in a single overcurrent device.
It states (a) terminate in a "device" and if you look up "device" in Art 100 it seems to cover panelboards; and (B) the calculated load must not exceed the ampacity.
I don't like it, but from reading, I'd say the Code would allow you to terminate in a MLO panel if your calculated load allowed.
240.21 says that conductors shall be protected where they recieve theyre supply they are recieving theyre supply off of another wire. Finish reading the article and tell me what the exceptions are because the exceptions look to me like the tap rules but idk maybe my book is a misprint