So u are sharing neutrals? Do u need to?I’m figuring home runs from the panel to be MWBC then when I get near the loads I’m going to run 12/2 mc for each circuit .
So u are sharing neutrals? Do u need to?I’m figuring home runs from the panel to be MWBC then when I get near the loads I’m going to run 12/2 mc for each circuit .
We can share neutrals but they must be #10 so since we run #10 home runs from the panel im going to run MWBC home runs out to various areas with boxes then branch out with 12/2 mc to all loadsSo u are sharing neutrals? Do u need to?
The advantage of doing that (using all #10's and MWBC's) is that you can run a larger conduit and stuff it with more conductors. The derating won't affect your 20 amp circuits until you exceed 19 circuits in a single raceway.We can share neutrals but they must be #10 so since we run #10 home runs from the panel im going to run MWBC home runs out to various areas with boxes then branch out with 12/2 mc to all loads
You don't use a 10D nail for handle tie? 10 AWG solid also works great.Typically I run EMT with MWBC's out of the panel to a point closer to the outlets and then transition to MC. In that case just 12/2 MC is typically used. Yes if you run MC all the way home you would need to meet that requirement for a #10 neuter.
A few comments on the handle ties. Note that you only need handle ties and NOT common trip for MWBC's. Three pole common trips are a lot more expensive than 3 single poles and a handle tie. The problem is some brands do not offer a three pole handle tie. When I use handle ties a don't install the center rod so someone can pull off the tie easily if needed to operate a single handle .
Those were certainly used on more than one occasion or so I understand.You don't use a 10D nail for handle tie? 10 AWG solid also works great.
The handle tie rule for MWBCs is a very dangerous rule IMO, I will not comply, or at least I will make so the tie can be easily removed.You don't use a 10D nail for handle tie? 10 AWG solid also works great.