Re: 10 sec transfer & 517
517.34(A) talks about having certain loads automatically placed on the generator after ?appropriate time-lag intervals.? Examples are central suction systems and compressed air systems that serve medial functions, sump pumps that are required for the safety of major systems, and smoke control systems. 517.34(B) then talks about having certain loads placed on the generator either automatically or manually. Examples include heating equipment for operating or labor rooms, certain elevators, and hyperbaric and hypobaric facilities (whatever they are :roll: ). The idea is that Life Safety and Critical get first priority, and the equipment branch has to wait until the generator has recovered from its start up and its initial loading.