Had a meeting with a client yesterday who's asking me to bring life safety lighting circuits to a panel which is backed up by turbines that need as much as 30 seconds to get running. I told him that we should have battery packs for the interim which he scoffed at stating that Article 700 has wording allowing you to take more than 10 seconds if you have such a situation.
I think he's dead wrong. 700(12)(5) says that you may use such a genererator if you have an auxiliary power supply for the interim - like a UPS.
Before I tactfully breach this subject with my client, I'd like to be sure I'm not missing anything.
What do you say?
thanks,