vw55
Member
- Location
- California
I have a proposed installation that has a 225A panel tapped to a 400A panel 500kcmil feeder via 4/0 conductors. The 225A panel is provided with main lugs only, no main breaker.
The designer has indicated that this installation complies with 240-21(b)(1), the 10' tap rule.
My question is whether the intent of 384-16 can be circumvented using the tap rule. The 225A panel has no over current protection.
Another aspect of this installation is that the designer is using two 42 circuit sections sub-feed lug connected for each of the panels indicated and total connected load for both panels calculates 375A with spare breakers provided.
The designer has indicated that this installation complies with 240-21(b)(1), the 10' tap rule.
My question is whether the intent of 384-16 can be circumvented using the tap rule. The 225A panel has no over current protection.
Another aspect of this installation is that the designer is using two 42 circuit sections sub-feed lug connected for each of the panels indicated and total connected load for both panels calculates 375A with spare breakers provided.