#10 wire on 1000 amp fuse?

Status
Not open for further replies.

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I am reviewing a set of drawings that show a fire pump and jockey pump. Basically, there is a #10 tap from the fire pump service to the jockey pump. This seems to be allowed if the tap conduit is encased in 2" of concrete (per 696.6(D)). Am I correct?

Another question about 695.4(1). The overcurrent protection must be sized for the locked rotor currents. Is there any limit to the size of the OCP? If I don't know what the locked rotor currents are, can I just make the OCP so large that I know it can handle the locked rotor currents? And can i do this without upsizing the wire?

More details:

There is a second service from the outdoor utility transformer to the fire pump disconnect (350KCM wire). The service goes to a 1000A fused disconnect. The disconnect feeds a wireway (again with 350KCM wire) where the tap is made. The 350KCM continues to the fire pump, and the #10 goes to the jockey pump.
 
Re: #10 wire on 1000 amp fuse?

The conductor to the fire pump motor and other equipment is 125% of the FLA per 695.6C. From what you are saying you have a 1000 amp fused disc feeding #350 cu to the pump. If so, would not the 1000 amp disc be the OC device for the pump?
 