is it legal to back feed a 100 a breaker in a 42 ckt pnl
my buddy said 30 ckt max...
who's rite ?
my buddy said 30 ckt max...
who's rite ?
Dennis Alwon said:I think the OP is asking more about the number of circuits in the panel.
It does not matter. I can have a 100 amp breaker feeding a 40 circuit 200 amp main breaker panel. It is fine as long as the load is suitable for the 100 amp breaker. I can add another 40 circuit sub panel and it could still be okay if the load is still under a 100 amps.
I would ask your friend where he got the 30 circuit rule from.
templdl said:It is my understanding that it must be listed as such by UL. If one were to take a MLO and add a 100a breaker w/ a lock down kit it the modification UL list. Does the modification void its UL label.
I can't recall that the NEC has anything to do with other than what's included in Art 110 regarding the listing of the panel and applying as directed by the manufacturer etc..
LawnGuyLandSparky said:100a main or 100a MLO in a 20/40 is very common.
You could buy a main lugs panel, and install a 100 Amp main in that.donselectric said:100a 30 ck around here...
thats why i want to back feed a 100 in a 42 ckt pnl