I need a sanity check. I am QAing a job and a feed to a 100 amp panelboard is 4#1 THHN, #8G in a 1.25" EMT.
Table C.1 in Appendix C claims you can put up to 4 #1 in a 1.25" EMT. I wanted to check if you can stick a #8G in there as well.
When I did the calculation, I struggle to see how you can even put 4#1 in the 1.25" EMT.
#1 THHN cable has an area of 0.1562 squared inches according to Chapter 9, Table 5. Multiply by 4 and you get 0.62 squared inches.
A 1.25" EMT has an area of 1.5 squared inches.
0.62/1.5 = 41.33% > 40% allowed fill!
What am I doing wrong here??
You need to look at note 7 to chapter nine tables. 1-1/4 " emt under the 40% fill column is .598 divided by the inches squared for each # 1 thhn (.1562) = 3.83. Note seven allows you to go to 4 conductors.
Good point however throw in the #8 egc and it is not compliant.
BTW(to the OP), you do know that an egc is not required unless it is speced
Note 7 does not help the present situation. It applies only when all conductors are the same size. We have four phase conductors the same size, and one EGC a different size. So I agree that a 1.25" EMT is not large enough for this set of conductors.
But I have another problem with this design. A #3 THHN has sufficient ampacity for a 100 amp load. This design uses a conductor that is two sizes larger than that. Do we not need to upsize the EGC, per NEC 250.122B?
I think Conduit was responding to the OP's question on the original install that did not have the egc.
I realize what Conduit was saying. But the OP was not talking about an install, but rather about a design, and the design does include the EGC.
@Dennis Alwon,
How is the EGC not required? It's a new panelboard. What will I bond the ground bus bar in the new board to? A new grounding electrode?
@charlie b,
Yea, I also thought it was oversized. However, 110.14(C)(1)(a) states that for
"circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following
(1) Conductors rated 60 deg C
(2) Conductors with higher temperature ratings, provided the ampacity of such conductors is determined based on the 60 deg C ampacity of the conductor size used
So, from that I inferred that for circuits 100 amps or less I need to use the 60 degree C ampacity column to comply with code regardless of the insulation temperature rating.
But I have seen 100 amp circuits with #2 & #3 conductors in the past, so it seems unclear.
@Dennis Alwon,
If the panel board terminations are known and they are 75C then you may use the 75C column for circuits under 100 amps. Look at (3)