Re: 100 Amp Panel Breaker Capacity
I just had an inspector tell me that the maximum number of breakers that a 100 amp panel can have is 12. Could this be remotely true?
In general, most of the main breaker panels sold have configurations of 20 circuit/100 amp, 30 circuit/150 amp and 40 circuit/200 amp. (I believe the 100 amp panels are available in smaller configurations). If you are using panelboards (bolt-in breakers) they are available in up to 42 circuits.
Sq D also makes a 200 amp main breaker, 30 slot - 40 circuit panel which they consider a "remodel" breaker panel. If you look at the buss bar, the bottom five breaker positions on each side are stepped (as awayne mentioned) making it acceptable to install tandem breakers in those positions and giving you the possibility for 40 s/p circuits. In addition, if you look at the breaker directory on the panel cover it displays the top 30 breaker positions with plain white rectangular slots in which to write in an identification. The bottom 10 slots have a dashed line through the center of the rectangular box for an "a" and "b" identification.
In a recent kitchen remodel job I added a wall oven and 2 counter receptacle circuits. The homeowner had an older 100 amp Sq D QO panel with several tandem breakers already installed. There was enough room to install the breakers I needed to but when the inspector looked at the panel he red tagged it and required me to either prove that the panel was designed to accept tandem breakers or install a sub-panel (his tip-off was the directory on the panel door). I installed the sub-panel even though the original panel (mechanically) accepted the tandem breakers. So not all buss bars are stepped.
the tandems won't fit unless you remove the metal tab on the tandem breaker
Awayne, be careful what you post here. Not all of us on the list are licensed electricians whose livelihood depends on "doing things right" and "doing right things".
Regards,
Phil
[ May 14, 2004, 06:22 AM: Message edited by: goldstar ]