100 Amp Service
cjcrawfo
What is the smallest conductor size that can be used on a 100 amp service? Contractor plans on using 3- 3/0. I think they might be a bit off on their plans.
Re: 100 Amp Service
The service entrance conductors are sized for the calculated load. If the calculated size does not correspond with a standard size, the next standard size can be used.
Is the 3/0 copper or Aluminum?
Is there a concern with voltage drop?
Is it a single family or commerical service?
Re: 100 Amp Service
3/0 copper is good for 200A at 75 degree C. Are you sure the plans didn't call for #3 AWG, which is good for 100A at 75 degrees C?
Re: 100 Amp Service
Just got a call from the A/E grp. They meant to make it a 200 amp service. All is well once again. Thanks for your help guys!
[ June 14, 2004, 04:24 PM: Message edited by: cjcrawfo ]
Re: 100 Amp Service
What do you mean by size of ground? Do you mean the grounding electrode conductor? This can vary depending on the particular electrode that will be connected. Section 250.66 requires a minimum of #4 for your GEC, but a #6 is all that is required for a ground rod connection.
Does that answer your question? :confused:
Re: 100 Amp Service
Sorry about all the confusion. Next time I post something I will be sure to have all the details in the original post. I kinda put the cart before the horse today. I ended up solving the confusion. Thanks again for your help.!