A 100A panel does not equal a 100A load. For some perspective my whole house never has pulled more than 80A. That is with double electric oven and two electric dryers.
Hello everyone,
I'm installing a 100 amp sub panel in a detached garage. The feed is coming from and 200 amp panel at the main house. The run is 80' long and will have three conduit bodies in it. My question is, would #2 copper be the correct conductor for this project? I'm using the 75 degree table to compensate for the ratings on the breakers. The cable will be THHN.
Thanks for all your help with this matter.
Best,Ken.
So considered a feeder but since it's not supplying the entire dwelling load no discount. We always use it and in the back of my head is worst case scenario put a 90 amp breaker in. (unless for some reason it has to be a 100)I checked the definition and I stand corrected. :ashamed: Thanks.