I have a 1200A regular service entrance breaker, so I cannot load it up to more than 80% of its rating.
If in the future the client wants to add load, can they replace it with a 100% rated 1200A service entrance breaker? Provided the service entrance conductors are 4 sets of 350 kCMIL.
This might be a silly question, but I wanted to triple check.
Thanks folks!