1000 amp DC breaker

Status
Not open for further replies.

TheJed

Member
Hello all,

Please see the attached picture of this 1000 amp breaker that was installed in an open frame as part of a -48vdc plant.
It does appear to have a plastic shield of some sort over the exposed lug connection points.

Does this approach align with the NEC code for mounting breakers?

I am concerned this is a safety issue.

Thanks for any input.
Jed-

breaker.jpg
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Hello all,

Please see the attached picture of this 1000 amp breaker that was installed in an open frame as part of a -48vdc plant.
It does appear to have a plastic shield of some sort over the exposed lug connection points.

Does this approach align with the NEC code for mounting breakers?

I am concerned this is a safety issue.

Thanks for any input.
Jed-

View attachment 21319
I don't recall there is anything in the code about how to mount a breaker. That would be a design consideration, or a UL listing issue perhaps.

Is 48 VDC considered hazardous where this is installed?

Is it otherwise guarded by a fence or locked doors, or some other effective physical means?

Is it under the control of a utility?

What makes you think it might be a safety issue?

personally, i would be most concerned about whether there was an adequate fault clearing path. I can't tell if there is one. A battery string can put out a LOT of current.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
I would say being 50 volts or less gets you some relief but I don't know how much as far as guarding and protection goes.
 