1000 amp gfi protection

Merry Christmas

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
what the code requires for 1000 amp or greater.
210.13, 215.10 or 230.95 depending on the circuit being a branch circuit, feeder, or service. Note that this only applies to solidly grounded wye systems having more than 150 volts to ground but not exceeding 1000 volts phase-to-phase.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
That may only be part of your problem. You need to assure the gear had acceptable NRTL certification.
 

wmthompson90

Member
Location
ky
Occupation
electrician
I started in the trade in 08. I’m still green I guess. I’ll google it after this reply. I don’t know what that is or recall it in a code reference.
 