rconteng said:I am wondering whether it will make a difference to a contractor if he were asked to pull five parallel runs of 4 conductor 1000 kcmil cable in 5" conduits vs 6 runs of 4 conductor 750 kcmil in 4" conduits. The distance is roughly 600 feet.
I am looking for 1,600 amps in total. According to the CEC in a buried conduit installation, 6 parallel runs of 750 kcmil aluminum or 4 parallel runs of 1,000 kcmil copper will do the job.don_resqcapt19 said:Why 6 runs of 750? That is way more ampacity than is 4 runs of 1000. Six runs of 500 would do the job.
the enclosures have a lot of space
chaterpilar said:Total cross sectional area of copper required to push 1600 amps to 200 metres is 1200 sq mm (with less than 2.5 % voltage drop).
now i believe 1 kcmil = 0.507 mm2,
so 500kcmil = 253mm2 so 5 runs of 500 kcmil should be enough.
Cheers.
infinity said:What does conductor cross sectional area have to do with ampacity when sizing feeders?
chaterpilar said:Total cross sectional area of copper required to push 1600 amps to 200 metres is 1200 sq mm (with less than 2.5 % voltage drop).
now i believe 1 kcmil = 0.507 mm2,
so 500kcmil = 253mm2 so 5 runs of 500 kcmil should be enough.
Cheers.
infinity said:What does conductor cross sectional area have to do with ampacity when sizing feeders?
chaterpilar said:Business of carrying current....
infinity said:Not really. Parallel 250 kcmil conductors are rated for 255 amps at 75 degrees C. A 500 kcmil THHN conductor at 75 degree C is only rated for 380 amps for the same equivalent circular mil area. That gives you two ampacities (510 amps v. 380 amps) for the same 500 kcmil of conductor. Trying to use an amp per circular mils formula to size conductors will not work.